Yes... 36v DC is rated at 700v AC, same with 220v AC wire, it is safe ?, this isn't described in my local codeThe lower voltage conductor is required to have the same insulation rating.
NFPA79: Wire insulation shall be identified and adequate for the voltage on that conductor.
Where the conductors are ran with or adjacent to other conductors, all conductors shall have the insulation rating for the maximum voltage involved.
l
Am I get benefit from twisting that cable ?Also preferably that each pair(s) of conductors of a shared conduit be twisted along their length.