Hi guys, I'm new to AAC. I reside in Malaysia which is currently running 220-240V mains voltage. I purchased a Toyozumi Step Down to operate 100V amplifiers I bought from Japan. This is the specs (I took it from the seller's site so have to remove the wordings):
As seen from the picture, I'm stuck at the 2 'grounds' connections. I referred here: https://incompliancemag.com/article/the-grounding-symbols/
I am uncertain to establish the connections so I need some clarifications before:
- The chassis ground (left) just like the name indicates, connects to the chassis /case in which the metal is enclosed?
- The protective earth, connects to where?
- 0 terminal should be connected to neutral?
- I want to place a circuit breaker (ELCB) before the primary, I use the calculations below to get amperage:
P=VI (PRI)
1800 = 230 * I
I=7.8A/ 8A
Is it the correct way to determine breaker amperage?
- I am placing another ON-OFF switch at the primary. Should I switch off the live (hot) wire only or both neutral and live?
Thank you for assisting me and have a nice day

As seen from the picture, I'm stuck at the 2 'grounds' connections. I referred here: https://incompliancemag.com/article/the-grounding-symbols/
I am uncertain to establish the connections so I need some clarifications before:
- The chassis ground (left) just like the name indicates, connects to the chassis /case in which the metal is enclosed?
- The protective earth, connects to where?
- 0 terminal should be connected to neutral?
- I want to place a circuit breaker (ELCB) before the primary, I use the calculations below to get amperage:
P=VI (PRI)
1800 = 230 * I
I=7.8A/ 8A
Is it the correct way to determine breaker amperage?
- I am placing another ON-OFF switch at the primary. Should I switch off the live (hot) wire only or both neutral and live?
Thank you for assisting me and have a nice day