How is this transformer giving 240V on the secondary?

Thread Starter

Mr.Potential

Joined Dec 4, 2019
17
Hi all,

Not sure if this is the correct forum but it's power related so the closest I could find.

If you look at the attached image of a transformer it states 120V to 240V, can somebody explain how you would get 240V out if the output taps are directly across one winding?

I can only assume that if the other winding was connected this would give 480V out (assuming the windings are matched). Is that correct or am i getting my knickers in a twist?

Cheers

Mitch
 

Attachments

ericgibbs

Joined Jan 29, 2010
21,390
Hi Mitch,
The transformer image shows the two Secondary windings in Parallel, this is done to increase the capable current output of the transformer.

Are you measuring 240V output when the transformer is connected as your image.?
E
Connecting the two secondary winding in series would give 480V, at approx half the possible current of the 240v version.
Note: when connecting secondary windings in series,Transformer.PNG the correct phasing of the two windings is important.
 
Last edited:

boostbuck

Joined Oct 5, 2017
1,034
Each secondary winding will be 240V, so connecting them in parallel will sum the current capability, as stated above in #2.

Connecting the secondaries in series will add the voltages, rather than the currents, so giving 480V as you surmise.
 

MisterBill2

Joined Jan 23, 2018
27,172
I get the impression from the drawing that this is a controls transformer. Then by definition it is intended to provide both isolation and voltage changing.
 