Hot neutral reversed in old apartment

Thread Starter

axxel

Joined Aug 9, 2014
4
Just bought an old NYC apartment built in the 60's. I believe it was updated in the 80's, but not really sure.

My surge protector indicated building fault wiring,and hot neutral reversed in all outlets except the kitchen and the window ac units, so I started doing a little investigating.

First, I wanted to verify I have a good ground to earth. I did not see any ground wires in my outlets, and suspect the outlet box is grounded itself. I ran a jumper from the circuit breaker box chassis to all of my outlet grounds and they all showed continuity. I think the grounds are all ok.

The first outlet that I wanted to inspect, that was indicating hot neutral reversed, I went ahead and pulled it out. To my surprise, the wiring colors look correct. The black is going to the narrow slot, and white wire to the wide slot. The odd part is that the kitchen outlet that tested good, also had the correct wire color polarity.

I then wanted to determine the polarity of my faulty outlet. I plugged an extension cord into the known good kitchen outlet, ran it and set it on the floor next to my reverse polarity outlet. I put my multimeter probe into the extension cord wide slot, and the other multimeter probe into the narrow slot on the faulty outlet, and I see no voltage. I remove the lead from the narrow slot and insert into the wide, and I see 124V. Thus, probing from wide to wide slot shows a voltage. To me, this confirms that the outlet has reversed polarity.

However, I am still confused as to why. Recall that all the wiring colors at every outlet were color coded properly (black going to narrow slot), but only a couple outlets had correct polarity voltage. Would this mean it was wired wrong at the circuit breaker box for most of the outlets and the others were done correctly? I have no way to tell, as I only have access to the circuit breaker switches, and cannot see any wiring, and am not going to attempt to pull the box out. It looks like it has not been disrupted in along time, and I am not going to do it myself.

Just looking for some input here. Wondering if I should just swap the wires that show hot neutral reverse, or have an electrician come out and look. It seems easy enough, but I am not sure if I could have more issues than I realize.

Thanks
 

inwo

Joined Nov 7, 2013
2,419
If you can find the outlet that's wired wrong and correct it, it will fix them all.

I wouldn't change the ones that are correct.

Find the problem one.;)
 

Thread Starter

axxel

Joined Aug 9, 2014
4
If you can find the outlet that's wired wrong and correct it, it will fix them all.

I wouldn't change the ones that are correct.

Find the problem one.;)
Interesting. I didn't think about that.

Any strategy to track that sucker down?

Basically, just pulling all of them that indicate reversed polarity, and find the one with INCORRECT color coding?

What about the fact that these are on different circuits. I would need to find the incorrect outlet on each one?

Thanks
 

crutschow

Joined Mar 14, 2008
38,534
It's, of course, possible that the wire is incorrectly connected at the breaker box, thus appearing to be wired correctly at the outlets.

In general, I don't know that interchanging hot and neutral is a significant problem. Most new two prong devices are double-insulated and do not have the two-prongs polarized (one blade wider then the other) so it becomes unimportant which is hot and which is mutual. The only appliances to be concerned about are those with a two-prong polarized plug and you can probably judge whether the design of the product would allow voltage to appear on any surface metal if there were an internal short.
 

Thread Starter

axxel

Joined Aug 9, 2014
4
It's, of course, possible that the wire is incorrectly connected at the breaker box, thus appearing to be wired correctly at the outlets.

In general, I don't know that interchanging hot and neutral is a significant problem. Most new two prong devices are double-insulated and do not have the two-prongs polarized (one blade wider then the other) so it becomes unimportant which is hot and which is mutual. The only appliances to be concerned about are those with a two-prong polarized plug and you can probably judge whether the design of the product would allow voltage to appear on any surface metal if there were an internal short.
It looks that way. So far, every outlet I've checked has proper color orientation.

I've read that tv's and computers may be sensitive to hot neutral reversed....
 

Kermit2

Joined Feb 5, 2010
4,159
It is doubtful any of your appliances will experience any problems, but it should be corrected none-the-less.

As a young boy long long long time ago. :)

I stretched out my arm and balanced on one leg in an attempt to close the refrigerator door. I was standing in front of the stove where I was warming up some chicken noodle soup. My leaning position required my body to come in contact with the stove. Of course since I was home alone, I was clad in only the minimum required clothing, wearing my tighty-whities.

The moment I made contact with the refrigerator door panel I received a nasty shock. The outlet into which the stove was plugged was reversed wired. It was a gas stove, but had a fancy, new at the time, electric sparking ignition feature. The installers had simply tapped into a junction box in the attic and wired it up. They were NOT true electricians, and for a long time no-one had discovered the problem because of the large distance between the stove and other appliances. The problem may never occur in your case depending on the electrical isolation conditions of your various appliances, but...

Now that you know about your problem, you should get it corrected if you can.
 

bladerunner

Joined Apr 15, 2012
83
=axxel;752643]Just bought an old NYC apartment built in the 60's. I believe it was updated in the 80's, but not really sure.

My surge protector indicated building fault wiring,and hot neutral reversed in all outlets except the kitchen and the window ac units, so I started doing a little investigating.

First, I wanted to verify I have a good ground to earth. I did not see any ground wires in my outlets, and suspect the outlet box is grounded itself. I ran a jumper from the circuit breaker box chassis to all of my outlet grounds and they all showed continuity. I think the grounds are all ok.

The first outlet that I wanted to inspect, that was indicating hot neutral reversed, I went ahead and pulled it out. To my surprise, the wiring colors look correct. The black is going to the narrow slot, and white wire to the wide slot. The odd part is that the kitchen outlet that tested good, also had the correct wire color polarity.
Follow these steps for this receptacle. Find the breaker that turns this outlet off. Turn it off and then check which other outlets are also turned off. This indicates all these are on the same circuit.. Map out all the outlets turned off, turn on the beaker and check all the outlets for polarity.

If all are bad polarity, you will have to pull all of the outlets on that circuit out. Be sure and turn off the breaker when you do this. While your at it, make sure your outlet box is grounded if it is metal. you should see the bare ground wire attached to the box not the receptacle. If they are all bad, simply change the white wire to the wide slot and the hot to the narrow slot.

If one outlet has a good polarity, the next outlet in line should be the problem. If the others are also of the wrong polarity, you will have to change them as well. Be careful and MAKE SURE. all are tight. A loose wire will start a fire.
 