MisterBill2
- Joined Jan 23, 2018
- 18,508
REloadRon made a very good and VERY IMPORTANT comment back in post #5. A fire suppression system is a LIFE CRITICAL SYSTEM and thus it is not a place to be adding any circuitry that is not approved by the equipment manufacturers. I would start with those diodes, 1N4007, rated 1000PIV and only one amp forward current.Wat to low a current rating for a life criticl system.
And certainly a fire system is no place for diodes across coils, because those are supervised circuits, meaning that there is always a small current running in one direction to monitor wiring integrity and in the opposite direction for alarm signalling. So your inverse diode is a short circuit in the test mode. I realize this makes it a lot more complex, but better to get it from me than some grouchy fire system inspector..
There is probably a correct and working way to have two systems drive one solenoid valve, but it is not as shown. There are solenoid valves with dual coils, or it may need two valves in parallel.
And certainly a fire system is no place for diodes across coils, because those are supervised circuits, meaning that there is always a small current running in one direction to monitor wiring integrity and in the opposite direction for alarm signalling. So your inverse diode is a short circuit in the test mode. I realize this makes it a lot more complex, but better to get it from me than some grouchy fire system inspector..
There is probably a correct and working way to have two systems drive one solenoid valve, but it is not as shown. There are solenoid valves with dual coils, or it may need two valves in parallel.