Fusing of mains - how many fuses needed?

Thread Starter

btebo

Joined Jul 7, 2017
100
Dear Fine Folks of ACC,

I'm feeding 220 VAC into a transformer to step it down to 110 VAC.

Both 220 VAC lines have their own separate fuse.

Do the two output lines of transformer (110 VAC) need to be fused F3 AND F4?

upload_2018-8-16_15-10-37.jpeg
Thanks!
 

Hymie

Joined Mar 30, 2018
1,347
You need fusing where a fault would otherwise result in an excessive current flow, resulting in a hazardous situation.

In the absence of tests (conclusively demonstrating this), I would recommend that the two phase fuses remain, protecting against an earth fault within the equipment, but you only need one fuse in the transformer secondary – protecting it from an overload. You might be able to omit this fuse, if it can be shown that one of the phase fuses will operate as a result of a secondary overload/short circuit.
 

MaxHeadRoom

Joined Jul 18, 2013
30,716
You only need fusing in both (F3, F4) if you do not re-reference the secondary to earth ground to set up a neutral.
If setting up a neutral, one terminal of the transformer is connected to the service ground and the conductor from that terminal is the neutral and unfused.
Otherwise both fused is the normal practice.
(NFPA79-NFPA70)
Max.
 
Last edited:

MaxHeadRoom

Joined Jul 18, 2013
30,716
Whenever I wired an industrial control transformer such as this, I would always set one up as neutral, unless there was circumstances where it was not practical etc.
Max.
 