A four-pole breaker would be three-phase plus neutral. It is guaranteed not to trip when all four circuits are at 25A. As with all breakers, it will probably trip when any of the circuits exceeds about 40A or 50A - see the curves in the datasheet.Hello AAC community
Not sure i posted this under the right forum but I'll go ahead and see the reaction. If a 4 pole breaker is rated 25A does it mean i can connect 4 single 25a load to each pole or my entire load must not exceed 25A ?
They are pretty common in 3-phase systems, they are used where you need to break all 3 phases and the neutral.I've never heard of a 4-Pole Circuit-Breaker.
Can You provide pictures and/or part-numbers ?
.
.
.
https://www.ecmweb.com/national-ele...ing-and-bonding-of-separately-derived-systemsIf you wish to use a separately derived system, you must use a 3-pole transfer switch for a single-phase, 3-wire system, or a 4-pole transfer switch for a 3-phase, 4-wire system [Art. 100 definition and Sec. 250-20(d) FPN No.1].
I've never heard of a 4-Pole Circuit-Breaker.
But yet they sell them at your local Lowes store. They are an available thing to extend the circuits in a too small breaker panel. They also make and sell twin breakers for two circuits in one slot.This may be done in some countries, but not in the USA.
Most of us think the 4th pole is for neutral. You have 3 hot outputs. You can have three 25A loads if you are connecting line to Neutral. In the US that is three 120V loads. You could also connect Line to Line and have less outputs at 220V.If a 4 pole breaker is rated 25A does it mean i can connect 4 single 25a load to each pole or my entire load must not exceed 25A ?
Then show me where the TS stated his breaker is 3phase. 3phase wasn't brought up until post #3 then everyone ran with that. The TS still hasn't been back with what type breaker he has. And his asking about what load each individual breaker/switch is good for makes my answer as good as all saying 3phase, since he never mentioned common trip.You should only Power a 3-Phase-Load with a "Common-Trip" Circuit-Breaker.
( 3 or 4 Poles )
Individual Breakers should be used for "Single-Phase" ( Hot plus Neutral ) Loads.
.
.
.