Hi for an auto car wash i need to specify 2 contactors for the following

" Two of the outputs from the plc are to contatcors which are both operated from 24v dc and which make / break the following loads

1 The motor which drives the pump for the spray and is rated at 230v 500w
2 The heater is rated at 400v 5kw"


Im looking to suggest the following Hager contactor for number 1 as its rated at 230v am i right in suggesting this??
http://www.hager.co.uk/product-cata...relays-contactors/contactors/esc464/46603.htm

But im struggling to find a 400v contactor, any suggetsions?

Thank you in advance
 

MaxHeadRoom

Joined Jul 18, 2013
30,562
That contactor you show has N.C. contacts, I imagine you need N.O.!
I assume the No 1 is a 1ph motor? or both 3 ph?
The first (1) is any small motor contactor for No 2 I would look for a Special Purpose contactor, these are used for loads with repetitive switching, that load (2) is only around 12.5 amps, 400vac contactors are fairly common as this is a common 3ph motor voltage.
Max.
 