Big fans on dairy farm

Discussion in 'The Projects Forum' started by ritzfarms, May 16, 2015.

  1. ritzfarms

    Thread Starter New Member

    May 16, 2015
    5
    1
    I just bought 2 big 1.35hp fans to hang in my freestall. They run off 220. I have a 220 line going to the freestall from my barn cleaner which I don't use anymore. I want to put in 1 box/switch to run both fans plus wire the fans. I've done general wiring in the house. Is this something I can do.
     
  2. MaxHeadRoom

    Expert

    Jul 18, 2013
    13,143
    3,622
    It is virtually no difference, except instead of dealing with a live and neutral, you have two live conductors, both of which must be fused and switched.
    And include a earth ground conductor.
    Max.
     
  3. crutschow

    Expert

    Mar 14, 2008
    16,506
    4,440
    Is the circuit breaker and wire size sufficient to operate both fans at the same time?
     
  4. ritzfarms

    Thread Starter New Member

    May 16, 2015
    5
    1
    The barn cleaner motor was 5 HP and 230 of barn cleaner chain. These are 2 new 1.36 HP fans that run easy. So I would say no problem. I hope
     
  5. BR-549

    Distinguished Member

    Sep 22, 2013
    3,042
    740
    I'd like to see that barn cleaner. We had to shovel, scrape and wheelbarrow twice a day.
    I never saw one.
     
  6. Reloadron

    Well-Known Member

    Jan 15, 2015
    2,066
    881
    I would come in through one of these Heavy Duty Steel Disconnect Switches and below that use a few motor starter switches with thermal overload. This way you can run individually if the need ever arises. Run everything in conduit and meet or exceed any regulations, such as here in the US NEC code and NFPA requirments.

    Ron
     
  7. ritzfarms

    Thread Starter New Member

    May 16, 2015
    5
    1
    Were shoveling now while we put in a parlor
     
    BR-549 likes this.