..... secondary voltage to the load is 40 V.. at what load current? Theoretically, the load current can be 1150 / 40 = 28 Amps. BUT your transformer winding is WILL NOT handle that current - it's rated at 10 Amps. So, you can have a load current of 10 Amps @ 40 Volts = 400 Watts. This works out to be 400 / 115 = 3.5 Amps approx at the input.If a transformer is rated for a maximum winding current of 10 A, would it be permissible to operate it with a 10 A of input current when the secondary voltage to the load is 40 V.
...so it's not possible.so you're saying it is not permissible?