Yup.Oh, sorry I misunderstood. I am not doing a very good job in this thread so far.
I thought you meant to put the motor in wye configuration across 230V which would put (1/sqrt(3))*230V=133V across the windings.
But of course you didn't mean that. That is stupid. You don't even have 230V, that's the whole problem isn't it?
You meant put the 230V delta motor into wye so that you can connect it to 400V without any transformer, right? If so, then yes, I think that should work. (1/sqrt(3))*400V=230V so each windings should see the correct voltage it is rated for.
There is no wye/delta start circuit, correct?