Hehe, guilty as charged. It's hard not to appropriate some of his idioms. They're just too darn catchy and convenient.
Yeah he's petty good.Hehe, guilty as charged. It's hard not to appropriate some of his idioms. They're just too darn catchy and convenient.![]()
Yeah I thought of that. My idea was to just connect the 120 into both sides of the transfer switch, but then the stove dryer, and everything else that's 220 wouldn't work.As far as powering more things in your house - you could probably utilize the full capacity of your genset by bringing out the third leg and neutral as a separate feeder and splitting it into two 120V, 20A branch circuits. You just wouldn't be able to backfeed this into your household wiring.
Thanks!Very simple answer, WYE connected generator. So you will have 120V from any phase to neutral, 208V between phases and still a limit of 52.5 amps absolute. Power output is 15kw/root2 or around 9kw but could be pushed slightly higher as long as individual line amperage doesn't exceeed 52.5/1.414 or about 35 amps. Math may be a little rusty but that is what you have without converting to DC and back using a VFD capable of 25kw 3 phase load and assuming said vfd can be operated single phase out!
Your limits are 120v single (5kw), 208V single at under 10kw or with appropriate VFD 15kw 120v single (7.5kw) 15kw 240v. I do not know where you can get a VFD programmed to output that way but they should exist as it is only software driven. Another option is an autotransformer if you require 240v but still limited to 10kw at 240, 5kw to neutral.
Root(2) is used for converting AC RMS to AC peak & vise-versa. Root(3) is used for 3 phase calculations.Slight math error, full load amperage / root2 or 1.414 to get max individual phase to neutral. 52.5/1.414=37.12A for single phase to neutral or another single phase ie 120 or 208V. Almost 50 years since 3 phase math by Avro Arrow engineers at college. This was one of the easiest subjects they taught!
10kW serving line-to-neutral loads only - 12.6kW if using 52.5A. E.g. 120V loads.Right, should have used root3 and generator is connected WYE thus the 120/208 rating. Still we have overcomplicated a relatively simple question. Personally I would approach this as 15kw 3 phase will give 10kw in a single phase configuration and if the 208V was too low, use an autotransformer to get what you need. One College instructor got frustrated and cancelled a 3 hour lab to teach us how to do quick approximations and get close when close mattered. Anyone who missed it was lost for the semester!
My approach is use quick conservative figures then if necessary work out the essential details. You have a small mine with 1.1MW installed motor load but most are 25-30% larger than mins due to starting and reserve needs. Your 800KW set runs at 650-700KW with the plant at peak production. Worst were conveyors with motors twice as big as necessary which caused power factor to be a consideration.
Neutral reference has nothing to do with it. Add 32V to 208V derived from two legs of a four wire wye system and you'll get 152 volts line-to-neutral on one leg. Totally unacceptable for supplying a 120:240V generator inlet. You'll fry half the loads in OP's house. The only way to pull it off is with a transformer at every single load that needs strictly 240V, and that sort of installation is not suitable for this application unless OP wants to wire up transformers to his clothes dryer, water heater, etc. every time the power goes out.Correct, autotransformers must reference to neutral. Lots of experience with them but I omitted that part. My problem is that I often assume others have a higher level of knowledge or experience than I should. Many of the shortcuts I take make no sense without a thorough knowledge of theory and practice.
Anyone want to delve into CD ignition systems! 100+ amps thru a 10 amp SCR but that is not what causes them to fail. Hint, dv/dt!
Use 120/208 or trade for a single phase genset.The only way to pull it off is with a transformer at every single load that needs strictly 240V, and that sort of installation is not suitable for this application unless OP wants to wire up transformers to his clothes dryer, water heater, etc. every time the power goes out.