But if there is a current overload on PCB, you don’t want the wiring to fail, you want the fuse to blow or breaker to disconnect.Why are you all giving the TS so many different answers? Facts are far better answers than opinions.
In post#1 he mentions a foot of 24AWG wire and a DC 3Asupply. In post #5 he mentioned that the load current is 1.5A max.
24AWG wire has a resistance of 25.67Ohms/1000ft. Therefore 1.5A will cause a voltage drop of 38.5mV over 1ft. of wire. That will be 58mW of power. That's definitely not enough to cause a dangerous temperature in the wire!
Of course it is VERY SAFE to use 24AWG wire in this case!