Oops, good catch.12Kw-Hours.
Max.
How about this one 25kw heater operating across three phase 460v what is the current draw?1500 x 8 = 12kW
I did do the math 5 times and got 54.35 using the same formula P=I*V 54.35 now Im seeing other use a different formula and getting 31.41 and wanting to know why they are getting this.I just realized this post was in the "homework help" forum. You should have done the math for the first one yourself instead of having the answer given to you.
Anyway, 25kw is the power, you have the voltage, and you're looking for current. P = I*V, so 25,000W = I * 460v.
You are correct, that gives you 54.35 AMPS (watch your units!)
Matt
Do you agree I should of used √3 formula?I think that last answer is incorrect for s 3phase system.
It also depends on the power factor.that runs non stop for 8 hours