P Thread Starter PAULSINCLAIR Joined May 3, 2017 12 Feb 13, 2018 #1 Hi, I have 240v 3 phase supply (no neutral). I have x3 single phase motors, will the below work? each Z being a 240v single phase motor.
Hi, I have 240v 3 phase supply (no neutral). I have x3 single phase motors, will the below work? each Z being a 240v single phase motor.
L LesJones Joined Jan 8, 2017 2,357 Feb 13, 2018 #2 I think it should work providing your 3 phase supply is 240 volts phase to phase. (This would be about 140 volts phase to neutral if you had a neutral.) Les.
I think it should work providing your 3 phase supply is 240 volts phase to phase. (This would be about 140 volts phase to neutral if you had a neutral.) Les.
P Thread Starter PAULSINCLAIR Joined May 3, 2017 12 Feb 13, 2018 #3 yes 240v phase - phase, no neutral Thanks
P Thread Starter PAULSINCLAIR Joined May 3, 2017 12 Feb 13, 2018 #4 Can anyone else confirm this? thanks
L LesJones Joined Jan 8, 2017 2,357 Feb 13, 2018 #6 One point. I am assuming the 3 phase supply is a normal 3 phase source. Do NOT do it if it is the output from a VFD. Les.
One point. I am assuming the 3 phase supply is a normal 3 phase source. Do NOT do it if it is the output from a VFD. Les.
MaxHeadRoom Joined Jul 18, 2013 19,186 Feb 13, 2018 #7 +1 on the agree. It has traditionally been done all the time. Max.