MaxHeadRoom
- Joined Jul 18, 2013
- 30,860
The 13A plug advantage is the internal fuse, each device can be suitabley fused as opposed to the typical N.A. system.Hi Max.
The 13A plug is still in use as the basic electrical mains power plug.
The 13A plug advantage is the internal fuse, each device can be suitabley fused as opposed to the typical N.A. system.Hi Max.
The 13A plug is still in use as the basic electrical mains power plug.
What I see as the primary advantage of the fuse in the appliance plug, instead of in a central circuit breaker panel, is that EVERY TIME the fuse fails, a replacement fuse needs to be installed. And as for the super-safe insulated plugs, certainly they add quite a bit of cost to every appliance. BUT HOW WELL do they protect against accidental shorted circuits in any of the wires in the walls?? OR is there a second fused panel at some main distribution panelnear the power entrance??The 13A plug advantage is the internal fuse, each device can be suitabley fused as opposed to the typical N.A. system.
hi,WELL do they protect against accidental shorted circuits in any of the wires in the walls?? OR is there a second fused panel at some main distribution panelnear the power entrance??

They don't protect against shorts in the wires in the walls, the breaker in the distribution board does that. But it does allow a lot of sockets to be wired on to a single circuit fused at 32A without requiring cable between socket and appliance capable of 32A. The 32A circuit is wired in a ring of 2.5mm^2 cable with each end returning to the breaker, so that each socket it effectively fed by two cables in parallel.What I see as the primary advantage of the fuse in the appliance plug, instead of in a central circuit breaker panel, is that EVERY TIME the fuse fails, a replacement fuse needs to be installed. And as for the super-safe insulated plugs, certainly they add quite a bit of cost to every appliance. BUT HOW WELL do they protect against accidental shorted circuits in any of the wires in the walls?? OR is there a second fused panel at some main distribution panelnear the power entrance??
As eric explained, the way I remeber it is there is also a breaker in the panel, similar to N.A.What I see as the primary advantage of the fuse in the appliance plug, instead of in a central circuit breaker panel, is that EVERY TIME the fuse fails, a replacement fuse needs to be installed.
There would have to be a breaker in the panel, as the incomer is 80A or 100A and the circuit is rated at 32A. There's also a RCD (which you call a GFI)As eric explained, the way I remeber it is there is also a breaker in the panel, similar to N.A.
Originally the home I am in had 60 amp service. Originally built about 76 years ago. Today pole to house, 240 VAC split phase I have 200 amp service and a 200 amp breaker panel. Actually just about all new residential construction involves a 200 amp panel and service.Typically , in the more modest homes, yje main breaker is either 60 amps or 100 amps. Then below that are one or two higher arted breakers, one for the electric stove and one for the electric water heater(for those folks with money to burn), followed by a pair of 20 amp breakers for the kitchen and 15 amp breakers for most other rooms. BUT, I have done work in homes with a higher rated main breaker and a total of 40 breakers . Bigger homes, with the filter system for the outside pool in one corner of one basement. A rather larger house. TWO 50gallon gas water heaters, side by side, also.

Interesting. When I lived in Italy we had a beach villa about 25 miles (about 40 Kilometers North of Naples. While the villa had a circuit breaker panel with 15 amp breakers the entry had a 20 amp breaker so the villa was limited to 20 amp max. I guess for a certain electric rate (cost) Enel (the power company) limited the power.Hello,
In holland we only have a 32 Amp main fuse for the 230 Volts entry.
For higher power a 3 × 25 Amp is used for homes with a heatpump or other higher power stuff.
Bertus