Urgent transformer paralleling problem

Thread Starter

Sraj123!

Joined Jul 11, 2023
4
Good Morning,
Before paralleling 2 dyn11 individually loaded transformers i got the following measurements;
A-A = 250V
B-B = 250V
C-C = 250V
A-B = 465v
B-A = 465 v
C-A = 465 v
would you please advise what would be the problem
with thanks
 
Last edited:

schmitt trigger

Joined Jul 12, 2010
772
The voltage relationship between phase to neutral and phase to phase. The sqrt(3) ratio is not being met.
Assuming that this is actually a three phase transformer, which I don’t know because THE PROBLEM IS that you haven’t told us.
 
Last edited:

Thread Starter

Sraj123!

Joined Jul 11, 2023
4
I don't see any problem mentioned in your posts, so how am I supposed to know what problem you are concerned about?
When i do phasing checks phase A to phase A should be close to 0, however i am getting 250V, and phase A to phase B should
be 415V, but in this case i am getting 465V.
That is why i posted this to get some solutions as to why i am getting these results. Is it because the neutrals of one of the transformers is causing this problem or can it be something else.
 

LowQCab

Joined Nov 6, 2012
3,580
The most likely problem is your measuring technique, or,
You are guessing at a Transformer for which You have no Specifications.

Please provide a picture of any specifications printed on the Transformer,
or better yet, provide the manufacturers Specification-Sheet.
.
.
.
 