I have a transformer rated 230V to 12-0-12V, 500mA.
i wanted to know what this means and what happens when i put a small load?
ex- If i add a load of 10 ohms what happens?
 

crutschow

Joined Mar 14, 2008
34,452
It means the maximum RMS output current rating of the transformer is 500mA.
You should never add a load that draws more than that amount of current.

If you add a 10Ω load between one output and the center-tap then the current through the load will be 12v/10Ω = 1.2Arms, which is over double the transformer rated current, and will rapidly cause it to overheat and burn out.

You need to study Ohm's law.
 

Thread Starter

ABHINAV ANAND

Joined Apr 7, 2018
2
Who
It means the maximum RMS output current rating of the transformer is 500mA.
You should never add a load that draws more than that amount of current.

If you add a 10Ω load between one output and the center-tap then the current through the load will be 12v/10Ω = 1.2Arms, which is over double the transformer rated current, and will rapidly cause it to overheat and burn out.

You need to study Ohm's law.
You think i dont know ohm's law??....i was wondering if coil will burn or mcb will trip.
And for the record....answer kindly next time.
 

MisterBill2

Joined Jan 23, 2018
18,519
CC is correct. Voltage over resistance equals current. And with a transformer that has a center tapped secondary, as indicated by the 12-0-12, a ten ohm resistor across the winding would actually draw 2.4 amps, and the transformer would be way overloaded. So a study of fundamental circuit theory is also in order.
 