I am working on an experiment to determine if the use of a DC controlled proportional AC relay has any detrimental effect on the system as a whole and the Quattro Inverter/Charger in particular. The relay has two amperage control modes burst and phase angle, my test uses burst mode. The relay is designed to control resistive loads only.
Test Environment:
Inverter/Charger: Victron Quattro 48/5000/70-100/100 120V (In Inverter Mode)
Battery BMS: Victron Lynx Ion BMS 1000
Batteries: Two Each Victron 24V/200AH HE NMC batteries wired in series.
Proportional Relay: Crydom PMP2425W (25A Rating)
PLC: Automation Direct BR-DM1E-10AR3-D
Load: 1320W 120VAC resistive heating element (This was the only load active)
Link to the Crydom relay datasheet is below:
http://www.crydom.com/en/products/catalog/pmp-nova22-proportional-control.pdf
My problem is an anomaly I discovered when the relay was set at exactly 50% output. Upon further testing I noted that this behavior existed when the relay was set to produce between > 45% and < 55% output power. At these settings the relay was sending exactly one cycle power off and one cycle power on. At all other settings the number of power on/off cycles does not match. Also, in the problem range, the power was firing when the Voltage passed 0 going negative; for all other output percentages, the power fired when the Voltage passed 0 going positive.
What drew my attention to this is a RMS voltage drop of about 4V in the problem range.
QUESTION: I don't have a clue what is causing this, or if there is any way to mitigate it. Any help would be appreciated.
Oscilloscope traces for 25%, 50%, and 75% output power are below:
The scope setup is:
Channel A (blue) is Voltage measured at the inverter. (Active/Differential Voltage Probe)
Channel B (Red) is Amperage measured at the relay output (Load). (Clamp AC/DC Amperage Probe)
25% Trace:
50% Trace:
75% Trace:
Test Environment:
Inverter/Charger: Victron Quattro 48/5000/70-100/100 120V (In Inverter Mode)
Battery BMS: Victron Lynx Ion BMS 1000
Batteries: Two Each Victron 24V/200AH HE NMC batteries wired in series.
Proportional Relay: Crydom PMP2425W (25A Rating)
PLC: Automation Direct BR-DM1E-10AR3-D
Load: 1320W 120VAC resistive heating element (This was the only load active)
Link to the Crydom relay datasheet is below:
http://www.crydom.com/en/products/catalog/pmp-nova22-proportional-control.pdf
My problem is an anomaly I discovered when the relay was set at exactly 50% output. Upon further testing I noted that this behavior existed when the relay was set to produce between > 45% and < 55% output power. At these settings the relay was sending exactly one cycle power off and one cycle power on. At all other settings the number of power on/off cycles does not match. Also, in the problem range, the power was firing when the Voltage passed 0 going negative; for all other output percentages, the power fired when the Voltage passed 0 going positive.
What drew my attention to this is a RMS voltage drop of about 4V in the problem range.
QUESTION: I don't have a clue what is causing this, or if there is any way to mitigate it. Any help would be appreciated.
Oscilloscope traces for 25%, 50%, and 75% output power are below:
The scope setup is:
Channel A (blue) is Voltage measured at the inverter. (Active/Differential Voltage Probe)
Channel B (Red) is Amperage measured at the relay output (Load). (Clamp AC/DC Amperage Probe)
25% Trace:
50% Trace:
75% Trace: