omron H3CR-H8L

Thread Starter

Martyk

Joined Jul 23, 2009
76
Hello

I am looking for the schematic for Omron H3CR-H8L timer relay.
Has anybody reverse-engineered this or similar units?

Tks
MartyK
 

Attachments

Jerry-Hat-Trick

Joined Aug 31, 2022
864
looking for the schematic for Omron H3CR-H8L timer relay
Hi, is it okay to ask why? Looking at the datasheet it's from 2010 and whilst the block diagram gives a fair idea of how it works you probably wouldn't do it the same way 22 years later. They aren't that expensive to buy so replacing a broken one in an otherwise functioning control system is probably the safest simplest option but if it's just set at one delay time and the exact accuracy is not so important a simple analog circuit would probably do the job. You could do all sorts of tricks if you use a processor.
 

Thread Starter

Martyk

Joined Jul 23, 2009
76
Hi Jerry

I don't know where you live, but here in Canada it is a VERY expensive unit (>$200).
The problem is it is not releasing.
 
Last edited:

strantor

Joined Oct 3, 2010
6,875
2022-2010=12
The problem is it is not releasing.
I would start the list of likely causes with "relay contacts welded shut."
Does it ever open? Like if you leave it unpowered for hours and come back, the contacts are still closed? If so, I would open it up and replace the PCB-mount relay that I assume is inside.
 

Thread Starter

Martyk

Joined Jul 23, 2009
76
2022-2010=12

The relay is in top shape. It is a bi-stable device which only needs a pulse to close and a pulse to open.
The unit will work ok for months and then just stay closed. I assume the opening pulse never happened.
It is something in the control cct: pulse too short?
I guess nobody has reverse-engineered this timer.
 

Thread Starter

Martyk

Joined Jul 23, 2009
76
Hi, is it okay to ask why? Looking at the datasheet it's from 2010 and whilst the block diagram gives a fair idea of how it works you probably wouldn't do it the same way 22 years later. They aren't that expensive to buy so replacing a broken one in an otherwise functioning control system is probably the safest simplest option but if it's just set at one delay time and the exact accuracy is not so important a simple analog circuit would probably do the job. You could do all sorts of tricks if you use a processor.
Why? So I can repair it. This is a true power-off delay, so a simple analog circuit will not work.
 
Sorry to hear that it’s still giving you grief. Could you share with us what you are using it for, what signal is used to toggle the relay on and off and do you need to set different delay times or is it fixed? Since the relay itself is still working I would consider replacing the circuit with a small processor to send the signal to the relay and, if you could provide more detail I’d be happy to suggest an approach
 

Thread Starter

Martyk

Joined Jul 23, 2009
76
Thanks for the reply Jerry.
I am not looking to change the circuit, just repair the unit.
FYI this is a true power-off delay relay. IE it starts timing after the power is removed. It uses a bi-stable relay that only requires a pulse to release, max 12 minutes. Occasionally, the release pulse never happens, so it stays ON forever.
When I said the relay is ok, I meant the internal relay, not the unit.
Don't know if this is a good explanation.
Thanks.
 
Ok, my first step would be to reduce the delay time and see if it still sticks. The device relies on the charge held on a large value electrolytic capacitor or even a super capacitor to trip the relay which can degrade over time. In fact, perhaps a good idea to replace it anyway if you’ve already opened the box. It should be pretty obvious which component that is. If your delay time is long the capacitor may have discharged too much by the time it’s asked to do its job
 

Pyrex

Joined Feb 16, 2022
577
Thanks for the reply Jerry.
I am not looking to change the circuit, just repair the unit.
FYI this is a true power-off delay relay. IE it starts timing after the power is removed. It uses a bi-stable relay that only requires a pulse to release, max 12 minutes. Occasionally, the release pulse never happens, so it stays ON forever.
When I said the relay is ok, I meant the internal relay, not the unit.
Don't know if this is a good explanation.
Thanks.
Hi,
Omron provides the block diagram.
Imho, something's wrong with the power failure detection circuit or with the power supply circuit. It is possible, you just need to check the electrolytic capacitors in these parts of the circuit. If you have an in-circuit ESR meter, it would be useful to check capacitors with it without even desoldering them
 

Thread Starter

Martyk

Joined Jul 23, 2009
76
Pyrex:
Are you able to troubleshoot a circuit from a block diagram? Not me.
If the unit is powered off and timing, the power supply & failure detection circuits are not active.
 

Thread Starter

Martyk

Joined Jul 23, 2009
76
Hey Jerry
I don't believe it is the big capacitor because it works ok for months at a time (several cycles/day).
It is most likely a borderline signal amplitude. Need the schematic to trace this.
Thanks for your help.
 
Electrolytic capacitors degrade slowly and the intermittent behavior could be related to ambient temperature - the leakage goes up with increasing temperature. For simplicity, if you can’t analyze what is happening it’s a cheap and quick fix to try replacing It. The cause could be electrical noise which makes the onboard processor think that power is still applied but that would probably be a frequent issue rather than months without a problem. Can you track the failures to probable ambient temperature? How long has the device been installed? How long is your delay off time?
 
Located in my heated basement.
Time = 2 min.
It's been running for many years.
Problematic soon after installing it.
Okay, that’s something different entirely. If it wasn’t working reliably from the beginning it’s probably not the device itself but the installation. Maybe induced voltage on the power input pins which can make it think it’s still connected to power if something close by is electrically noisy. What voltage is powering it and what is the relay connecting? Maybe something like a pump to keep water flowing after a boiler turns off to stop the heat exchanger from overheating?
 

Pyrex

Joined Feb 16, 2022
577
Pyrex:
Are you able to troubleshoot a circuit from a block diagram? Not me.
If the unit is powered off and timing, the power supply & failure detection circuits are not active.
First of all, what type of ICs can be seen on the PCB? I'll guess that it's CMOS, the 4000 series.
Secondly, it's not hard to find where the power supply circuit is. Look at what the power supply pins are connected to, they are probably connected to a diode bridge or to a single diode. Behind that diode (or bridge rectifier) there will be a high-capacity electrolytic capacitor, this is the one that should be checked first. Most likely, there will be an integrated voltage regulator, a 7805' or something similar.
The power failure detection circuit is also connected to the same pins or to same diode, it could be built on a 4000 series IC or on a comparator or an op-amp. I happened to see a similar circuit built on 4000 series ICs, with a small capacitor at the input of the IC and its load resistor. The time constant of the capacitor and resistor was small because the voltage drop needed to be detected quickly. (The 3.3 or 4.7uF capacitor had dried out) .
In short, so we don't have to guess, it would be better to take a photo of the PCB, at least one photo with good resolution from both sides of the PCB
 

Thread Starter

Martyk

Joined Jul 23, 2009
76
Okay, that’s something different entirely. If it wasn’t working reliably from the beginning it’s probably not the device itself but the installation. Maybe induced voltage on the power input pins which can make it think it’s still connected to power if something close by is electrically noisy. What voltage is powering it and what is the relay connecting? Maybe something like a pump to keep water flowing after a boiler turns off to stop the heat exchanger from overheating?
Power: 24vAC, approx 6ma (from the spec sheet)
How can there be induced voltage at 2 minutes of no power?
I have 2 installations that use this relay. In both cases, it prevents a compressor from cycling too fast, and the loads are switched by a second relay, not the timer directly. If I interchange them, the problem follows.
 

twohats

Joined Oct 28, 2015
621
Hi Martyk,
A lot of guesswork going on here.
16 Posts before we get any idea what its being used for.
If it isn't getting the correct signals, can you blame it for giving you grief?
Good luck..............
 

Thread Starter

Martyk

Joined Jul 23, 2009
76
Hi Martyk,
A lot of guesswork going on here.
16 Posts before we get any idea what its being used for.
If it isn't getting the correct signals, can you blame it for giving you grief?
Good luck..............
There is no signal input. It starts timing when the power is removed.
 
Since you have two, one which works fine and one which has an intermittent fault maybe you can troubleshoot by checking the voltages in the same places on the PCB on each to spot if there is a difference. As suggested by Pyrex in #16 photos of the PCB would be good, as well as IC part numbers and component names and values you can read. Since the fault follows the device it’s not external as I expected, but I still suspect capacitors as they are typically the weakest link in electronic devices. Monitoring the voltage across the large capacitors after power is removed may show a difference between the units
 