Ohhh, that makes a lot of sense. Is there a reason it has to be a 2k ten turn pot, or similar? For example I know it would allow me to vary my resistance to obtain a higher gain (or lower), but couldn't I also calculate the resistance it would take to be at 100 degrees C. Then I would calculate the voltage and then apply a gain that does let me hit the voltage input limit (or near it) of the U3?OK, then I would consider the following. Make a bridge about like I drew it. When choosing Rg (Gain Resistor) I would look around for a 5 K ten turn or even better 5 K twenty turn trimmer pot. With about 1.6K the Rg will get you close to 212 Deg F = 2.4 Volts. As to actually checking the temperature you can try using some crushed ice and distilled water and make a Ice Bath Slurry as best you can. While not perfect it will be close. Next place the sensor in a pot of boiling water and adjust your Rg for 2.4 Volts. Again, unless you are at sea level under ideal conditions it will not be 100 C but will be close enough. That should give you a zero and span. Do not connect to the analog input channel until Rg is adjusted. I am guessing these devices have some form of input protection?
Actually this 2K ten turn pot would be a good Rg.
Ron
I say this because the RTD's are already firmly set on the Heat Pumps, and to get someone to uninstall one to so I could calibrate it would be difficult.