See if this diagram helps make sense of the latching leakage path.
On the left, both controller outputs are closed, so both relays close and all works as expected.
On the right, controller number 2 has opened its output, but the voltage from the left side of relay 2's contacts leaks through (the blue path) which continues to apply power to the whole right leg which is meant to be controlled by controller 2.
With power still present in this leg on the right, relay 2's coil is powered, so the contact doesn't release. Since the contact doesn't release, the leg on the right is still powered. Can you tell that this paragraph is a recursive loop that never ends?!?! It's latched!
Once this latching state has occurred, the only end to it is if BOTH controllers open their contacts at the same time. That would remove the source of power for the latching behavior.