Hi.
After two decades my family could finally build an electric line to the farm, giving a rest to the old diesel engine and to our pockets as each day running the irrigation pump would burn 200L of fuel. Now a whole month running the pump 24/7 will cost 1/4 of a day with diesel.
Unfortunately, one day we found a fuse had blown, without any load (see attached image as an example of the fuse, although this is a three phase line). My father (they live alone there now) replaced it but the power was not restored, as apparently other fuse was blown 4km away and another one 10km away. He replaced them all, and again they blew up within 5 minutes: first the one on the transformer, then the one 4km away, and then the one 10km away. This situation repeated itself, sometimes with days between fuse blowouts, sometimes minutes. If the pump is running the fuses will not trip.

The motor is ok, the transformer is ok and line to ground isolation is ok.
The line is 20km long from where it got to originally, with 10m tall poles, separated 80m each with 60cm between conductors and we are its sole consumers. It is in a remote rural area and has no transpositions, nor capacitors or inductors. its voltage is 13.2kV, our transformed rated at 40kVA, the motor consumes 23kVA when working and the HV fuses are 8~12A.
Distance to the substation is about 40km.
The transformer manufacturer told us there could be an issue with line capacitance blowing the fuses, as the transformer is fine, and that transpositions along the line would solve the issue.
What do you think about this?
Thank you very much
After two decades my family could finally build an electric line to the farm, giving a rest to the old diesel engine and to our pockets as each day running the irrigation pump would burn 200L of fuel. Now a whole month running the pump 24/7 will cost 1/4 of a day with diesel.
Unfortunately, one day we found a fuse had blown, without any load (see attached image as an example of the fuse, although this is a three phase line). My father (they live alone there now) replaced it but the power was not restored, as apparently other fuse was blown 4km away and another one 10km away. He replaced them all, and again they blew up within 5 minutes: first the one on the transformer, then the one 4km away, and then the one 10km away. This situation repeated itself, sometimes with days between fuse blowouts, sometimes minutes. If the pump is running the fuses will not trip.

The motor is ok, the transformer is ok and line to ground isolation is ok.
The line is 20km long from where it got to originally, with 10m tall poles, separated 80m each with 60cm between conductors and we are its sole consumers. It is in a remote rural area and has no transpositions, nor capacitors or inductors. its voltage is 13.2kV, our transformed rated at 40kVA, the motor consumes 23kVA when working and the HV fuses are 8~12A.
Distance to the substation is about 40km.
The transformer manufacturer told us there could be an issue with line capacitance blowing the fuses, as the transformer is fine, and that transpositions along the line would solve the issue.
What do you think about this?
Thank you very much