With everything disconnected to the meter, I get zero Ω across the +- of the current input on the back of the trumeter. I checked it with 3 different DMM. I checked the input next to it which is the voltage input to see what it was and it was also zero Ω. Possibly this is a bad meter from the factory.
Sense the CT seems to be working right, (is it normal for it to be 4.8mA instead of exactly4?) and peaks out around 22 mA at startup, I am thinking its something with this meter. I have gone over my wiring so many times, like you said its fairly simple. When I put a DMM in place of the trumeter I am getting close to the correct mA readings that I should be. So if things were wired wrong I wouldn't see something else or perhaps nothing at all.
Sense the CT seems to be working right, (is it normal for it to be 4.8mA instead of exactly4?) and peaks out around 22 mA at startup, I am thinking its something with this meter. I have gone over my wiring so many times, like you said its fairly simple. When I put a DMM in place of the trumeter I am getting close to the correct mA readings that I should be. So if things were wired wrong I wouldn't see something else or perhaps nothing at all.