Is it okay to interconnect copper bonded earthing electrode with the GI Earth strip?
Thread Starter Sai Krishna Betha Joined Apr 26, 2021 1 Apr 26, 2021 #1 Is it okay to interconnect copper bonded earthing electrode with the GI Earth strip?
Ya’akov Joined Jan 27, 2019 9,170 Apr 26, 2021 #2 Welcome to AAC! Copper and zinc are quite far apart on the galvanic series, they are not compatible, particularly in the presence of moisture. This paper has some information:https://www.researchgate.net/figure...es-to-which-LPS-materials-are_fig10_282924315
Welcome to AAC! Copper and zinc are quite far apart on the galvanic series, they are not compatible, particularly in the presence of moisture. This paper has some information:https://www.researchgate.net/figure...es-to-which-LPS-materials-are_fig10_282924315