I have a MAC 45A-AA1-DACC-1BA solenoid valve rated for continous duty at 24VAC 7.7VA holding / 10.9VA inrush. Measured current at rated AC voltage is about 340mA and coil resistance is 24.3ohms. I want to control the valve using a relay. On the oscilloscope large spikes were seen when the relay contacts open. Adding an RC snubber in parallel with the solenoid reduced the observed spikes on the oscilloscope. I then tried a transparent relay to see if there was a visual reduction however I unfortunately still noticed sparking when the contacts open. After trying various combinations of RC values, a bidirectional TVS by itself, TVS together with the RC snubber, and the TVS on the relay contacts, sparks on opening still occured.
I read mixed reviews about running AC relays/solenoids with DC. Some on this forum have referenced this article where it is discouraged. Other articles such as this seem to hold more favorable views:
For hobbiest grade use what are your opinions of running AC solenoid valves on DC (assuming one already has an AC valve on hand)? It looks like it can be beneficial in terms of power dissipation/heat and controling relay sparking.
I read mixed reviews about running AC relays/solenoids with DC. Some on this forum have referenced this article where it is discouraged. Other articles such as this seem to hold more favorable views:
I tried running my solenoid valve and at 9V DC and its drawing 335mA which decreases to about 300mA after one hour. The valve body temperature after one hour is around 40c compared to about 60c when run at rated AC. I haven't observed any magnetic issues with the coil sticking. Finally using a simple diode I no longer visually see any sparking when experimenting with a transparent relay.Will there be any benefits associated with the DC operation? Yes, you can expect coil life to be extended three-fold due" to the [+ or -]70% power reduction. In addition, you'll have clean, solid make-and- break operation with no contact chatter, hum, or buzz.
For hobbiest grade use what are your opinions of running AC solenoid valves on DC (assuming one already has an AC valve on hand)? It looks like it can be beneficial in terms of power dissipation/heat and controling relay sparking.