HI
I AM CHECKING IN 3 HP NEW MOTOR WINDING RESISTANCE FOR COIL TO COIL =8.8 Ohms
but ohms law is telling 3 hp motor resistance is 76.95 ohms why.....
 

ericgibbs

Joined Jan 29, 2010
18,849
Hi,
Something is causing a hiccup, in post move operation.
Looking into it.
Mod.

I expect you saw that the original Thread is 5 years old.!
So a new Thread was Created, for the new poster in order to clear the Thread hijack
 
Last edited:

crutschow

Joined Mar 14, 2008
34,438
The motor resistance determines the stalled rotor current (starting current), not the running current.
A running motor generates back EMF which reduces the current.
The running current is determined mainly by the motor load.
 

CBTech_Joe

Joined Sep 9, 2020
39
The motor resistance determines the stalled rotor current (starting current), not the running current.
A running motor generates back EMF which reduces the current.
The running current is determined mainly by the motor load.
Yup, this is spot on.
The windings in a phase to phase measurement (all three in a three-phase motor) should read low but not zero ohms. The smaller the motor, the higher this reading will be, but it should not be open. It will usually be low enough (under 30 Ω) for the audible continuity indicator on your meter to sound.
Testing a motor phase to phase only has value if you suspect unbalanced current loading. Each phase to phase reading should be within a few percentage points of each other.
 
The OP has not stated the motor technology so far!
Max.
You are correct. I thought I read 3 phase, but I see all he stated was 3 HP.

So, my information is only pertinent to a 3 phase induction motor which does happen to be the most common format for motors. If however OP has something different, then all bets are off.
 