5 Pole, 3-phase
JWHassler
Joined Sep 25, 2013
308
Get a couple of good wirepeople to replace the existing (probably green) wire with a green/white pair and wire it right.
Otherwise you'll be on the hook for the next shock/fire that happens within 100 feet and/or five years.
gerty
Joined Aug 30, 2007
1,305
If you open the door of your distribution panel and it says 120/208Y then you do in fact have a neutral.
Using the ground as a neutral (current carrying conductor) is a code violation, and if there are exceptions that are out there please give chapter/verse
Dave0707
Joined Apr 14, 2015
8
Okay, so my panel reads 208y/120 ; 240; 240/120(delta). So as Gerty said, I should have a neutral and a ground in my distribution panel. Since the majority of my run from box to the twist lock is in conduit, I can add that 5th wire through it and connect it to the ground so I can have a L-L-L-N-G, and just change out the service cord to a 5 wire.
Dave0707
Joined Apr 14, 2015
8
Thanks to all you guys, that is exactly what I needed to know. I will try to have this done in the next week or 2. Thanks again!
alfacliff
Joined Dec 13, 2013
2,458
here we have all machines bonded together, individual ground rods can cause ground loops which can be disasterous in fault situations. one common ground is the recomended way.