I am stuck on a question similar to the delta question I asked:
Three devices are connected in wye to a three-phase four-wire 240 Volt supply.
I know that the neutral current will be the vector difference of currents ABC.
First I need to find the currents:
Ia= 240/_0 deg / 30 /_25.84 = 8_/-25.84A
Ib=240/_120 / 20/_36.87 = 12_/83.13A
Ic=240/_240 / 10/_0 = 24/_0A
Next I find the difference between the currents:
In= 7.2-j3.49 - 1.435+j11.91 - -12-j20.78 = 17.765+j12.36 = 21.64/_34.82A
The answer given for the question is 14.6A????
Three devices are connected in wye to a three-phase four-wire 240 Volt supply.
- A-N Z = 30 ohms pf = .9 leading
- B-N Z = 20 ohms pf = .8 lagging
- C-N Z = 10 ohms pf = 1
I know that the neutral current will be the vector difference of currents ABC.
First I need to find the currents:
Ia= 240/_0 deg / 30 /_25.84 = 8_/-25.84A
Ib=240/_120 / 20/_36.87 = 12_/83.13A
Ic=240/_240 / 10/_0 = 24/_0A
Next I find the difference between the currents:
In= 7.2-j3.49 - 1.435+j11.91 - -12-j20.78 = 17.765+j12.36 = 21.64/_34.82A
The answer given for the question is 14.6A????