Thermostat bad or OK

wmodavis

Joined Oct 23, 2010
739
Depends what kind of thermostat.

If you want/need a valid helpful answer you need to provide enough information to make that possible.

Otherwise I could just provide this answer - connect digital multimeter to thermostat and see if it is OK!
 

#12

Joined Nov 30, 2010
18,224
The old mercury bulb, 4 wire thermostats were simple switches which connected red to green for fan, red to yellow for compressor, and red to white for heat. All the rest of the logic and power switching is done in the noisy parts of the equipment. These can be examined with an ohm meter.

Modern digital thermostats make the same connections but they are equipped (plagued) with time delays and resets that make checking all the triacs take nearly half an hour. You can not check them with an ohm meter. You have to apply 24 VAC and measure for an output voltage.

If you have a heat pump or a fuel burning furnace, the Blue and Orange connections come into play as logic signals to the change-over switches and valves. Which kind do you have?
 

MaxHeadRoom

Joined Jul 18, 2013
28,702
Many digital thermostats use a Miniature relay, if you can get it to operate around the set point, listen for the relay click, check the output with an ohm meter, if it stay open, it is usually the relay contacts shot.
Max.
 

strantor

Joined Oct 3, 2010
6,798
I have seen the honeywell relay thermostats as well, used in industrial water & hydraulic cooling units, but never seen them in residential applications.
 