I have an existing feeder in an MCC with an IPD TC100L gG fuse (100A) with a feeder cable with a derated CCC of 132A.
At first i thought it was okay as the fuse is rated at 100A but when I saw the fuse TCC I saw it starts at 140A @ 10,000sec. Does this mean this fuse will actually only start melting at current >140A? What happens between 100A and 140A? My cable is 132A so not sure if its protected at all.
This seems to be same the same for all fuse sizes, the TCC starts at a much higher current that the rated value, for a 160A the TCC starts at 210A!
How do you normally size a fuse based on your cable derated current capacity?
Many Thanks!
At first i thought it was okay as the fuse is rated at 100A but when I saw the fuse TCC I saw it starts at 140A @ 10,000sec. Does this mean this fuse will actually only start melting at current >140A? What happens between 100A and 140A? My cable is 132A so not sure if its protected at all.
This seems to be same the same for all fuse sizes, the TCC starts at a much higher current that the rated value, for a 160A the TCC starts at 210A!
How do you normally size a fuse based on your cable derated current capacity?
Many Thanks!