I am planning to make a soft start circuit since the Tranny I intend to use in my Big Daddy PSU is tripping my 10A CB.
The Tx is around 2000VA. It has 4 windings of 60V capable 8.3A Continues.
My PSU will have 4 outputs, all isolated so I can series them and parallel them if needed.
My question is simple.
What will you use for the series power resistor tht limits the inrush current.
I thought of series connecting 4 X 10Ω10W . So 40Ω 40W.
Will it do. What will u recommend for the delay time. 1 sec or more.
The smoothing caps will be 10,000μf . per winding.
The Tx is around 2000VA. It has 4 windings of 60V capable 8.3A Continues.
My PSU will have 4 outputs, all isolated so I can series them and parallel them if needed.
My question is simple.
What will you use for the series power resistor tht limits the inrush current.
I thought of series connecting 4 X 10Ω10W . So 40Ω 40W.
Will it do. What will u recommend for the delay time. 1 sec or more.
The smoothing caps will be 10,000μf . per winding.