I have a Ajax (out of business) 7.5hp, 230v, 39.5 fla, 1730 rpm single phase electric motor. The run capacitor blew and the motor would start and then blow the breaker. The numbers on the capacitor can not be read. I replaced it with one of the same physical size 25uf, 370/440v and the motor runs. I am concerned about motor damage based on internet posts about wrong size capacitors causing too high amps or low power. The nla with this capacitor is 13.6a. I have tried adding 5uf in parallel, and get 12.5nla, 10uf added in parallel gives 11.0nla and 15uf added in parallel gives 10.0 nla.
I also tried adding 5uf and 10uf to a pressure washer with a 15uf run capacitor. The run amps dropped with each addition in parallel
I have read some post in HVAC forums where they change run capacitors until they get the lowest amps. These tests were under load conditions. This does not seem to work?
Are there any other ways to determine the right run capacitor size?
I also tried adding 5uf and 10uf to a pressure washer with a 15uf run capacitor. The run amps dropped with each addition in parallel
I have read some post in HVAC forums where they change run capacitors until they get the lowest amps. These tests were under load conditions. This does not seem to work?
Are there any other ways to determine the right run capacitor size?