Protection 110 volt AC

Thread Starter

Hj sulaiman

Joined Sep 8, 2009
2
Hi , Every body.
I like to share the idea or if I was wrong correct me that to protection for 110 Volts A.C was identical device ,Earthleakage for used in 240 volt A.C . or any special protection for it. which mean that such as an electronic cut off etc.
 

Gustav180

Joined Aug 25, 2009
17
I can not se exactly what you think, but 110 V is not danger as 230 V. But it is danger enough to kill if you are sensivity. So you have to use the same protection circuits as for 230 V.

You have to use a low voltage, 50 V DC or 36 V AC to bee safty from electrical shocks

Best regards
Gustav
 

JoeJester

Joined Apr 26, 2005
4,390
You have to use a low voltage, 50 V DC or 36 V AC to bee safty from electrical shocks
In certain enviroments your body resistance can be as low as 300 ohms. That would make you unsafe to work on 50 V (167 mA) or 36V (120 mA) circuits. Greater than 50 ma can cause ventricular fibrillation.

Remember this ... the butt you save maybe your own. Be smart and be safe.
 