Power Dissipated Into Wire

Thread Starter

hitmen

Joined Sep 21, 2008
161
The impedance of the wire is (0.05 + j0.15)
The current through it is (97.6<-41.6688)(phasor)

Why cant we use the equation P = ZI^2 and expand everything out?
I got a garbage value.
 

The Electrician

Joined Oct 9, 2007
2,970
Does your text explain the difference between real power and reactive power?

The key to this question is the word "dissipated"; that means that they want the real power.

Try again, and show your calculations.
 

Thread Starter

hitmen

Joined Sep 21, 2008
161
Yes.

But my answer is P = Z * I^2
= (0.05 + 0.15j)Ω (97.6<-41.6688)A^2
= (0.15811<71.565)(9525.76<-83.3376)
= 1506.11794<-11.7726
= 1474.436 - j307.290 :confused:

This is nowhere near your answer. Is there something wrong with my concept?

Thanks!
 

Thread Starter

hitmen

Joined Sep 21, 2008
161
That should be real power.

Do you know the correct answer?

Is 97.6^2*.05 anywhere near the correct result?
Hi electrician:

Why are you using the magnitude of the phasor for the current and the real value for the impedance?

When is the time to use which?

Thanks!
 

The Electrician

Joined Oct 9, 2007
2,970
Only the real part of the impedance is dissipative. When current passes through the impedance, the value of the real part is what determines how much heat will be produced by the current.

The RMS value of the current is what you use in the formula P = R * I^2, and the RMS value is just the magnitude of the current phasor. Notice that I've used R * I^2 instead of Z * I^2 to remind us that it's the real part of the impedance that dissipates power.
 

Thread Starter

hitmen

Joined Sep 21, 2008
161
ok. In that case what is the imaginary part of the impedance used for?

Why does multiplying everything out like I have done give me the wrong answer?
 

The Electrician

Joined Oct 9, 2007
2,970
ok. In that case what is the imaginary part of the impedance used for?
It is used in determining the total voltage drop along the wire when the current in the wire is known; it's used for determining the reactive power, which is not dissipative.

Why does multiplying everything out like I have done give me the wrong answer?
Because when you do that you are including the reactive part of the line impedance in the calculation, and the reactive part doesn't contribute to the dissipative power loss. Also, you need to use the RMS value of the current, which is the magnitude of the current phasor neglecting the phase angle.
 

Thread Starter

hitmen

Joined Sep 21, 2008
161
Okay I get it. :)
Thanks.

But why does my lecturer use the formula P = ( Vmag)(Imag)cos(θv - θi)
And this time the real part is NOT taken :confused:
 

The Electrician

Joined Oct 9, 2007
2,970
It's just a different formula. It gives the same result as the method I gave you : 476.288 watts.

It's an example of what the reactive part of the line impedance can be used for.
 