Can you say what type of three phase voltage powers the unit is it WYE or is it DELTA?Hi all im trying to make a phase failure alarm for a 3 phase refrigeration unit. im struggling with what parts i need and how to get the low voltage output to trigger the siren
Phase failure protection is a little trickier than you might think. For example, if a 3 phase motor is running, and one phase goes down (perhaps a fuse blows), a relay connected from line to neutral, even on the dead phase, will remain energized due to a voltage from the other phases via the motor windings.Like R!f@@ said, if 240V Id use 3 relays 1 for each phase to neutral so contact closes if any one phase goes down & trigers the siren.
Whats wrong with this?Google is your friend..... http://www.drillspot.com/products/53143/Square_D_8430MPDV29_Three_Phase_Failure_Relay