You need to flip one of your zeners. They need to have either their anodes connected together, or their cathodes connected together (note Richard said back-to-back).Richard,
I appreciate your detailed advice.
I will connect the two diodes in series and insert in series between the lamp and the neutral line.As seen in the diagram.
Is there a way to test it?
My generator will fluctuate between 58 and 62. If the gen becomes overloaded it could maintain around 55Hz until the overload is gone.
'Twas not I who posted it.andersonmilltexas
Using zeners of a different voltage would be the best way to change the tripping characteristics. The wattage of the light bulb will have only a marginal effect and I would suggest using a small night-light bulb of around 5 Watts. With that bulb the worst-case current if the GFCI doesn't trip is 5/120 = 42mA, but the cold resistance will be only a few hundred ohms ( http://forums.x10.com/index.php?topic=18816.5;wap2 ) so it will only make a volt or two difference to the tripping threshold.
Your zeners should be rated such that they don't burn up if the GFCI doesn't trip (we expect it to, but don't want to create a fire hazard if it's faulty). Each one will dissipate 0.5*0.042*30 (for 30V zeners) = 1.3W, I would use zeners rated for roughly twice this.
Ron,
That's an interesting cicuit you have posted, that one monitors for excessive live-ground voltage which is useful but wouldn't detect an overvoltage due to lost neutral. It could be modified to separate the voltage being monitored from the tripping current.
It could be done with a microcontroller but I suspect that between powering the microcontroller and providing the tripping current the circuit wouldn't get any simpler. It would however allow you to program some time dependant tripping characteristic which would be a nice feature to have.
Oops.'Twas not I who posted it.
In that case either that "little connector" needs breaking off or two seperate outlets should be used.No. In the US, a receptical is always run as two loads on the same 120V phase unless you break off the little connector and run the wiring yourself or demand the electrician do that.
I agree that lost neutrals are probably quite rare, but they can be very destructive. It happens in the UK three-phase system occasionally causing 240V loads to receive 400V. In the US split-phase system the worst case voltage in the event of neutral failure is 2*normal rather than (√3)*normal and there are more places where such a fault can occur because split-phase is used domestically.ps, In general, I disagree with all this complication. I had an illegal splice in my neutral and lost a few devices, but after I repaired the illegal splice, everything is good, like several million other houses in the US.