Thank you marcf.There is a lot of info on the http link in my pdf attachment. This is what I knew as a "class B" alarm system. The EOL resistors (1k) need to be put at the end of the 2 wire line. The EOL resistors can be brought back to the panel, but this requires 4 wires. Class A systems use 4 wires and are capable of resounding alarm, trouble, and tampers.
A monitoring system using just NO COM switches only detects an open circuit for an alarm and is thus less capable than a system using NO NC COM switching.
Alarm: short across the loop, then loop opens.
Trouble: Open on the loop.
A tamper is like a trouble, but denotes some one is tampering, a trouble can be caused by a system, or device problem.
Most panels have the power (battery) isolated from the building power, but connect the panel to the building ground via a high resistance (1Meg). This allows the panel to detect a ground fault by monitoring the voltage at the junction of the ground fault resistor and a comparator.
Thank you marcf.http://tech.vyanet.com/Tech_2010DSC_PC3000_v74_Program_Sheet.htm
Try this one. Be advised that this web site is "http" (not secure) not "https" (secure).
This panel is a normal panel. A battery is used for operation and the AC line provides a charging source for the battery. The AC line and the power (battery)to the panel needs to be isolated form each other. One reason is that wire damage (shorting to EMT, crushed wires, etc) needs to be detected.
Also the terms NC an NO connections usually mean the relay, sensor is _NOT activated. There will be continuity from NC to COM and an open between COM and NO. For a 'fail-safe' operation, you would want the relay to be energized when their is power, thus NO would be closed not open. Hope this makes sense.
Do you mean when the door is opened it activates an existing light fixture or something else?I'm thinking to add a light sensor on the line of door sensor, what I like to use is Arduino unit at 5Vdc system
Thanks.Do you mean when the door is opened it activates an existing light fixture or something else?
How would that work when the door is closed and the wire is at zero voltsI was planning to add sensors such like light sensor, temperature sensor, which can work independently, no matter the door close or open just borrow the wires.
I'm confused, how does that tie in with the alarm wire from the door?if the door in close status, the connection will be like the picture shown
Thanks.https://www.mouser.com/ProductDetail/Texas-Instruments/P82B96P?qs=aEuGZpxfbxV0WPFsO7nJmg==&mgh=1&gclid=Cj0KCQiA_8OPBhDtARIsAKQu0gbApto6WUAqLUznUH5jbj5PSDg3LHk_cZs9YLsa6KNorMPhARHg4IsaAj2rEALw_wcB
I used this I2C range extender and it worked quite well for both 1wire and I2C.
Our old condo had a lot of CAT5 network and telephone cable installed. As we had cell phones, we did not need to use the phone cable and only need to use a few of the network lines, I tried to install several 18B20 1 wire temp sensors around the condo at the telephone / network jacks.
Talking to one sensor connected to any jack was successful , however when I tried to talk with more than on on different lines, this did not work too well.
When I used the p82b715 everything came together.
I needed to have 3 wires however. +5v, 0V, and data.
If you have 12v from the panel at the door alarm switches, you could use a 5v regulator.
If you only have the door switch available, then this approach would not work.
Not with a 12 volt alarm system.is it possible to replace all sensor to 5Vdc?
Thanks.Not with a 12 volt alarm system.
If you want to activate some kind of external device when opening a door or window using the existing sensors and wiring without interrupting the integrity of the alarm system then no problem as I showed in post #61. Other then that I don't see how you could do anything else unless you can connect to a unused grn/yel pair if it is accessible.
Most the magnetic door switches I have seen used are pressed fitted into the door jam. Using a small flat bladed screw driver or knife you can gently pry it out and usually be able to access the cable.
This was explained before.but, where the power wire red/blk goes? each cable has 4 wires and each sensor just used 2.
Thank you sghioto.This was explained before.
The door and window switches only use the red/blk pair.
The keypads require 4 conductors, red/blk for power and yel/grn for data
The motion detectors are similar, red/blk for power and the yel/grn to the com/zone terminals.
In your alarm panel you can see a bunch of unused yel/grn pairs bundled up.
Years ago when I did alarm pre-wiring for new construction we used 2 conductor cable for the door/window sensors and 4 conductor for what ever else required 4 conductors. Things like keypads, motion detectors, CO2 detectors, fire, glass break sensors, etc.
The people who installed your alarm decided to use all 4 conductor cable for some reason. Maybe that was all they had in the truck.