Hi,
I am trying to calculate the power of a machine by measuring the currents and voltages of the machine using Fluke 434/435. The machine is connected to a three-phase power supply. The information plate of the machine tool says the following information:
- Voltage: 400
- Phase: 3
- Hertz: 50/60
- Full load: 13 Amps
- Largest Load: 21 Amps
- Machine Total Power: 5.6 kW
The recorded data that I am getting is around
- V1: 413 Volt, I1: 68.1 Amps
- V2: 416.9 Volt, I2: 68 Amps
- V3: 415.45 Volt, I3: 70.1 Amps
- Active Power 39360 W
- Reactive Power 4346.7 W
- Apparent Power: 39786.7 W
- Power Factor: 0.78
- Crest Factor (for V1 V2 V3): 1.42, 1.41 and 1.41 respectively.
- Crest Factor (for I1 I2 I3): 2.13, 2.09 and 2.04 respectively.
- How it comes the maximum current of the machine is 13 Amps but I am getting about 70 Amps in each phase?
- Why the apparent power is nearly equal to the active power and both of them are far away from the machine total power?!
Please note that I set up the Fluke to record from Delta 3-phase circuit, but I am not totally sure if the circuit is in Delta or Wye configuration. How can I make sure?!
I would like to let you know that I have a limited background in electrical stuff. So, please consider that in your answer.
Thank you.
I am trying to calculate the power of a machine by measuring the currents and voltages of the machine using Fluke 434/435. The machine is connected to a three-phase power supply. The information plate of the machine tool says the following information:
- Voltage: 400
- Phase: 3
- Hertz: 50/60
- Full load: 13 Amps
- Largest Load: 21 Amps
- Machine Total Power: 5.6 kW
The recorded data that I am getting is around
- V1: 413 Volt, I1: 68.1 Amps
- V2: 416.9 Volt, I2: 68 Amps
- V3: 415.45 Volt, I3: 70.1 Amps
- Active Power 39360 W
- Reactive Power 4346.7 W
- Apparent Power: 39786.7 W
- Power Factor: 0.78
- Crest Factor (for V1 V2 V3): 1.42, 1.41 and 1.41 respectively.
- Crest Factor (for I1 I2 I3): 2.13, 2.09 and 2.04 respectively.
- How it comes the maximum current of the machine is 13 Amps but I am getting about 70 Amps in each phase?
- Why the apparent power is nearly equal to the active power and both of them are far away from the machine total power?!
Please note that I set up the Fluke to record from Delta 3-phase circuit, but I am not totally sure if the circuit is in Delta or Wye configuration. How can I make sure?!
I would like to let you know that I have a limited background in electrical stuff. So, please consider that in your answer.
Thank you.