house a/c generator

Thread Starter

samjesse

Joined Sep 14, 2008
212
Hi

How much horse power an electrical generator needs to run? I mean for an average house electrical needs.

are we talking about more than 5 to 10 or 10 to 50... horse power.

thx
 

beenthere

Joined Apr 20, 2004
15,819
Grab some figure for the electrical load, say 100 amps (most modern houses have 200 amp service). 100 amps X 120 volts = 12,000 watts. One HP is 748 watts, so 12,000/748 = 16.04 HP.

Nothing is 100% efficient, so figure more like 30 HP to run the alternator. One man in the 1920's rigged a Model T Ford engine to supply his electricity and hot water needs.

If you buy a generator set, the manufacturer will have a properly sized engine included.
 

MikeML

Joined Oct 2, 2009
5,444
In my house, just the bare necessities to get by include a refrigerator, a freezer, a few lights, and the gas furnace blower for a total of 5kW. Starting the induction motor in the furnace is the most problematic. The ratio of starting current to running current in a fractional horsepower induction motor (like in the furnace, fridge, and freezer) is about 15:1, so it takes large generator to provide the motor inrush current.
 