False Triggering on Solenoid Circuit

Thread Starter

Otto

Joined Dec 27, 2008
2
Need some suggestions on how to eliminate "false triggering" of the solenoid on the attached single line/block diagram. This circuit is installed in a house and operates as intended, but when an exhaust fan is switched on (in-rush) somewhere in the house, the solenoid is activated. Looking for a type of filter -or- suppression circuit to add to the original circuit. Thanks.........
 

Attachments

Alberto

Joined Nov 7, 2008
169
The block diagram doesn't say much! Important to know is the shematic of the infrared circuit and the solid state relay. Just for trail you could install a capacitor of 0.1 microfarad X2 rated on the secondary of both the tranformer, to block possible interference coming from the main.
If this is not enough, then a deep exam of the circuitry is mandatory.

Alberto
 

drc_567

Joined Dec 29, 2008
1,156
It sounds like the exhaust fan motor .... typically an induction motor, is causing a voltage instability either on the DC supplied board, or on the solid state relay. When an induction motor turns on, there is a large current drain that lasts for a few seconds. This event is likely the cause of the problem. Is there a sufficiently large electrolytic capacitor on the input to the DC supplied board? .... Such a capacitor might even out any temporary voltage anomaly. Check any wiring hook-up connections on the solid state relay .... no corrosion or oxidation .... use a contact cleaner spray ....
 

Thread Starter

Otto

Joined Dec 27, 2008
2
Thanks for the replies. I only have a hard copy of the schematic and my home scanner is not operational, so as sson as I get it up and running I will post the entire circuit. In the mean time I will try the capacitor....thanks again!
 