Hello,

Hoping this isn't too stupid.

I'm running 115Vdc from a Harris turbine (micro-hydro generator similar to a Pelton wheel) 700' to a charge controller. The maximum amperage would be close to 12.

Instead of running two wires could I run one 'hot' wire to the charge controller and run the other to a ground rod on each end. I've been told I can't by people I like but I'm not sure if that's true or why. I"m using #6 copper stranded wire for one lead, and if I need the other it would be #1/0 Al.

Thanks for whatever attention you can give this.

Regards,
Corky
 

dsp_redux

Joined Apr 11, 2009
182
Hydro-Quebec uses something similar to this on it's distribution network and uses earth ground as a ground. It really depend on how you are equipped, and how you can make it safe enough to be conceivable. This can be quite hazardous.
 

jad69

Joined Jun 5, 2010
1
12 amps ... all the earthworms may get pissed, but likely you can do it. to measure resistance of ground put a 12 volt battery or source at one end with an amp meter in series, measure the voltage across the wires at each end, as precisely as you can ( not at the battery as the amp meter can have significant drop) then post the numbers and wire length and size and someonw will calculate the ground resistance for you.
 