Current that a conductor

Thread Starter

bwd111

Joined Jul 24, 2013
117
can carry continuously without exceeding its temp rating would that be considered full load amperage? Because its running at full load
 

MaxHeadRoom

Joined Jul 18, 2013
28,686
The rating by the NEC/ANSI/NEMA rating is the continous current in amperes that the conductor can carry at without exceeding the temperature rating of the insulation which is stated as 60°C and 75°C type, the rating is also affected by whether the conductor is in a raceway or a control enclosure.
Max.
 