Hello to all and thank you in advance for any insight you can give me. I installed an outlet plug for my three wire 240v 30 amp air compressor today and when it turned on, I shut off the breaker to make sure I had the right circuit. I made the change, tried it and it was working fine. I did the same thing again, when it was running I tripped the breaker to reroute a wire. Now it will not work, nothing at all, not a sound. I have never used the breaker before to turn it off and am afraid I messed something up. It has power into the motor on the two hots according to my meter, pressure switch is fine. I tried the red reset button, spinning it by hand, and letting all air out. Please help.
 

#12

Joined Nov 30, 2010
18,224
Seems too simple from here. The 240 volts is being applied to the terminals of the motor and the motor doesn't even notice. The motor only has one job: to turn when 240 volts is applied to its power terminals, therefore, the motor has something wrong with it.

(Spinning it by hand removes the capacitor from the equation.)
 

Thread Starter

bigblock81

Joined Feb 24, 2013
6
Maybe I didn't say this right, I only moved the motor with a screw driver through the guard a few turns from where it was, not spun it over rapidly with power applied.

I guess I was looking for something easy. Maybe something simple I am missing.
 

#12

Joined Nov 30, 2010
18,224
Well, I bought a cheap compressor from Harbor Freight and the wire fell off the capacitor. It wouldn't start, so I looked at the wiring and found the problem without a meter.
 

Thread Starter

bigblock81

Joined Feb 24, 2013
6
Looks like I will do more detective work. Are both "humps" on the motor capacitors? I will look at all connections, and see if I can find instructions on how to test capacitors. I am an autobody tech with limited experience repairing ac motors.
 

JDT

Joined Feb 12, 2009
657
Probably. If you have two capacitors, one is the starting capacitor and the other is the "run" capacitor.

The starting capacitor is disconnected when the motor gets up to speed either by a centrifugal switch or an electronic circuit.
 

tinkerman

Joined Jul 22, 2012
151
Maybe I didn't say this right, I only moved the motor with a screw driver through the guard a few turns from where it was, not spun it over rapidly with power applied.

I guess I was looking for something easy. Maybe something simple I am missing.

Any sound from the motor when you apply power? If not there is an open circuit somewhere.
 
Last edited:

gerty

Joined Aug 30, 2007
1,305
Another thing fits your description. Are you using a double breaker?
If you are using two single pole breakers and when you "re routed" your wire, you picked another breaker on the same phase it won't run.
To check this put your voltmeter on ac volts and check across the two hots coming in. You should read your 220-240 volts. If you get no reading across the two hots, but get 120 to ground you have them connected to the same phase in the panel.
According to code you need to be using a double pole breaker, or tie the handles together( a piece of wire through the holes in the handles)
 

Thread Starter

bigblock81

Joined Feb 24, 2013
6
Any sound from the motor when you apply power? If not there is an open circuit somewhere.
No sound at all.

I will check about it being on the same phase. I ran out of room in my panel so I took out the regular 30 amp breaker and put in a space saver 30 amp breaker. It looked like it was on the same phase, so I will post my results.
 

gerty

Joined Aug 30, 2007
1,305
A space saver is 2 breakers on the same phase.

edit: for those that aren't familiar with space savers, they give you 2 circuit breakers in one slot. Which means they are on the same phase and cannot be used for a 220 volt application.
 

Thread Starter

bigblock81

Joined Feb 24, 2013
6
A space saver is 2 breakers on the same phase.

edit: for those that aren't familiar with space savers, they give you 2 circuit breakers in one slot. Which means they are on the same phase and cannot be used for a 220 volt application.

You sir are correct! When I bought the space saver breakers, one 30 amp and one 50 amp, the guy at the hardware store picked them out and said they would work for 220. WRONG! I should have stopped when it looked fishy as I was installing them and noticed they were on the same bar.

I am glad gerty looked outside the box!

I installed the old breaker and it works.

I did not know to measure between the leads for 220v. I only went from each lead to ground. Thank you for the lesson!

Thank you all for your input, I would have looked even more dumb taking the motor off and to a shop for them to tell me nothing is wrong with it!!:)
 

Thread Starter

bigblock81

Joined Feb 24, 2013
6
Yes, I threw you all off, I had no idea the breaker would have made this mess, I was too focused on the motor, and not what I had done. Lesson learned!
 