I found yet another manual for the whole Solar battery series range from BSB (the type of my batteries). It too says this:
"Constant voltage charging is recommended
Recommended float charge voltage: 2.27Vpc @20°C
Float voltage temperature compensation: -3mV/°C/cell
Float voltage range: 2.25 to 2.30 Vpc @ 20°C
Cyclic application charge voltage : 2.40 to 2.46 Vpc @ 20°C
Max. charge current allowable : 0.25C10A"
"And yet another manual for the same type of batteries says this:
Constant voltage charging is recommended
Recommended float charge voltage: 2.25VPC @20-25°C
Float voltage temperature compensation: -3mV/°C/cell
Float voltage range: 2.23 to 2.27 VPC@20- 25°C
Cyclic application charge voltage : 2.35V/cell
Max charge current allowable : 0.25C10A"
Even they can't make up their minds...
So according to this too I'm doing everything all right. Yet they're gassing...