battery monitoring circuit

Thread Starter

sujinvipin

Joined Aug 18, 2011
28
i would like to cal the fuse rating for the battery monitoring circuit.
i have attached the image.
Vinput=56V battery input and my desired vout to the plc input should be 9V.
i have chosen the resistances to be 5.6K and 1K ohm.
So by calculation i get the max current in the plc to be 6.6mAmps.
Now how would i determine the fuse rating. for eg if i take a fuse rating of 0.5A then would the plc be protected when the battery voltage is 56V.
 

Attachments

R!f@@

Joined Apr 2, 2009
9,918
Boy !! U are going to need very high power resistors and a container to keep them touching anything.

Ever consider getting a DC to DC converter
 

SgtWookie

Joined Jul 17, 2007
22,230
With the resistor values shown, you'd have ~8.5mA current flow through the two resistors, and you'd need a resistor rated 3/4W or higher for the 5.6k resistor. That's quite a bit of power to use just to monitor the voltage of the battery.

At a minimum, use 10x as much resistance to get the current below 1mA, and use a 10nF to 100nF cap from the junction of the resistors to ground to provide a low-impedance input to your PLC's ADC. Keep the ADC sample rate low so that the cap doesn't get drained needlessly. This will enable you to use 1/10 Watt resistors for both the 56k and 10k values. You will not need a fuse, as resistors don't fail shorted. Power dissipation in the 56k resistor will be ~50mW.

If you wish to further reduce the power consumption by the monitoring circuit, you can increase the resistors up to ~8.5 times more; 85k for the lower and 470k for the upper. This will give you roughly 0.1mA current through the two resistors, and ~8.58V at the junction of the two. If you then use a 10nF cap to ground from the junction, it will require about 8mS for the cap to fully charge, or 80mS for a 100nF cap to charge.

I've attached a schematic/simulation of the latter; only the time segment from 40mS to 80mS is shown.
 

Attachments

Last edited:

eblc1388

Joined Nov 28, 2008
1,542
You still need a fuse. A 0.5A or 1A one will do.

This is not needed for the resistors but will protect you from accidents like shorting of the DC 56V via whatever possible means, like using multimeter wrongly on current range while doing a voltage measurement.
 

Crispin

Joined Jul 4, 2011
94
...and use a 10nF to 100nF cap from the junction of the resistors to ground to provide a low-impedance input to your PLC's ADC. Keep the ADC sample rate low so that the cap doesn't get drained needlessly...
thanks!:D That answered a question I did not know existed. I was seeing this on my current project (400V -> 3V divider)