Hi all - I an an absolute beginner when it comes to grid tied inverters. I need help.
Background - I been using a cheap HF 45 Watt kit for battery charging and driving some 12v LED lighting around the house. I recently obtained a damaged 250W PV panel that still puts out ~8 amps @ Voc 32~34v. This is a lot more than I needed for the LEDs, so the perpetual student in me said I needed to find a use for this new found source of energy. The cheaper mostly foolish side me said why not try out one of those cheap chinese made GTIs. For not much more investment I might save a buck in the long...long...run. Well the first Sun500g was pretty much DOA. Its replacement seem better but still very "inefficient".. Finally here comes my first question. How should efficiencies be measured? ..let me continue a bit more and explain what I have measured and how... Then I will badly need your advice.
Today Jan 5, 2012 the ...
Peak Isc measured across the inverter dc input was 7.08 amps
Voltage measured across the inverter dc input was 28.5 volts
The current drawn (10A meter) in series with the panel and the inverter was 4.28 a.
The Kill-A-Watt meter between GTI and GFI measured 108 watts
My rusty math estimates the ...
Watts available at the panel near 7 x 28.5 = ~200 watts
Watts consumed by the GTI near 4.3 x 28.5 = ~123 watts
My newbe conclusion is that the ...
PV+GTI system's efficiency = 108 watts out / 200 watts available = ~54% while the
GTIs internal efficiency = 108 watts out / 123 watts in = ~88%
If my logic and math is not fatally flawed.. the question becomes ...why does the GTI take so little of the "watts available" and is there a GTI spec value that I should be aware of while I learn more about GTIs and PV systems. Thanks for staying with me
Thanks for any comment and advice.
Background - I been using a cheap HF 45 Watt kit for battery charging and driving some 12v LED lighting around the house. I recently obtained a damaged 250W PV panel that still puts out ~8 amps @ Voc 32~34v. This is a lot more than I needed for the LEDs, so the perpetual student in me said I needed to find a use for this new found source of energy. The cheaper mostly foolish side me said why not try out one of those cheap chinese made GTIs. For not much more investment I might save a buck in the long...long...run. Well the first Sun500g was pretty much DOA. Its replacement seem better but still very "inefficient".. Finally here comes my first question. How should efficiencies be measured? ..let me continue a bit more and explain what I have measured and how... Then I will badly need your advice.
Today Jan 5, 2012 the ...
Peak Isc measured across the inverter dc input was 7.08 amps
Voltage measured across the inverter dc input was 28.5 volts
The current drawn (10A meter) in series with the panel and the inverter was 4.28 a.
The Kill-A-Watt meter between GTI and GFI measured 108 watts
My rusty math estimates the ...
Watts available at the panel near 7 x 28.5 = ~200 watts
Watts consumed by the GTI near 4.3 x 28.5 = ~123 watts
My newbe conclusion is that the ...
PV+GTI system's efficiency = 108 watts out / 200 watts available = ~54% while the
GTIs internal efficiency = 108 watts out / 123 watts in = ~88%
If my logic and math is not fatally flawed.. the question becomes ...why does the GTI take so little of the "watts available" and is there a GTI spec value that I should be aware of while I learn more about GTIs and PV systems. Thanks for staying with me
Thanks for any comment and advice.