2/3 watt meter problem

Thread Starter

needs

Joined Mar 30, 2010
16
Hi,

I have problems on 3 phase systems,

what is the purpose of connecting the load star point to the supply neutral current while setting currents taken from supply?
 

t_n_k

Joined Mar 6, 2009
5,455
You tie the load star point to neutral to ensure the line-to-neutral load voltages are equivalent to the supply line-to-neutral voltages. A floating star point on an unbalanced (in particular) 3-phase load would lead to imbalance of the load line-to-star point voltages and hence unexpected load phase current values. It's sound procedure.
 

Thread Starter

needs

Joined Mar 30, 2010
16
Ohh Thanks very much!! i have another question when comparing results with the 2 or 3 watt meter methods, why is it necessary to disconnect the neutral?


thanks alot!!
 