Dear all,
I am trying to impliment the online calculator on excel sheet.
here is online calculator
http://www.bulkwire.com/wireresistance.asp
i follwed below method to calculate but i cant getting same answer http://www.rapidtables.com/calc/wire/voltage-drop-calculator.htm
can some one explain how to get value using below perameter as example
length of cable is= 50 feet
load current = 6A
source voltage =12v
consider 24 guaze wire perameter
diameter in inch given=0.0232 inch
diameter in mm is given as=0.590mm
resistance @77 deg F=26.18 ohm/ft
resistance @77 deg F= 85.9 ohm/km
how to calculate resistance for length;voltage drop; % voltage drop??
what are right perameter to be used to exact answers
DickCappels
Joined Aug 21, 2008
10,187
resistance of a length of wire in ohms = (ohms/meter) x (length or wire in meters)
voltage drop across length or wife = (resistance or length of wire) x current
% voltage drop = 100x ( voltage drop across length) / total applied voltage)
(some text removed for clarity)
The resistance in feet should be 26.18 ohms/1,000 feet
Your task will be easier if you choose one measurement system or another and stick with it. Ohms per km @ 77 °F looks kind of funny.
ajitnayak87
Joined Dec 30, 2013
9
Ok i am mentioned as defined in link. I dont know which value being used in calculator link . So I told using these perameter from link how can i get
output data :
resistance for length=1.30912
voltage drop =7.85472
out put voltage source drop=4.14
percentage loss= 65.46
Input parameter in calculator are
load current = 6A
source voltage =12v
gerty
Joined Aug 30, 2007
1,305
Dear all,
load current = 6A
source voltage =12v
24 ga wire will not carry 6 amps, good for 1 amp at best. According to calculator you'll need # 8 wire. And when figuring distance, don't forget the wire has to go from source load and back again. So a load 50 feet from source uses 100 feet of wire.
ronv
Joined Nov 12, 2008
3,770
Dear all,
load current = 6A
source voltage =12v
You cannot calculate it because the wire resistance is to high to allow 6 amps to flow at 12 volts.
The resistance of 100 feet of 24 awg is about 2.6 ohms so the most you could get with 12 volts is about 4.6 amps.