Using Hall Effect Sensor on primary side of Distribution Transformers

Discussion in 'The Projects Forum' started by Knigh7, Apr 24, 2015.

  1. Knigh7

    Thread Starter New Member

    Feb 25, 2014
    6
    0
    I'm doing my final year project related to load monitoring on distribution transformers. I was thinking of using Current Transformer to get the current readings at the primary side (11kV line), but one of my seniors advised me that I could use a hall effect current sensor instead, as it would make it much easier for me to use with a micro controller. I've done a bit of research on this but I'm not sure if its possible to use a hall effect current sensor at 11kv ?
    Can you please guide me if this is the right approach or should I look for another solution ?
     
  2. Alec_t

    AAC Fanatic!

    Sep 17, 2013
    5,813
    1,105
    The Hall sensor wouldn't connect to 11kV; it would, like a current transformer, be responding to the magnetic field generated by current in an 11kV cable.
     
  3. alfacliff

    Well-Known Member

    Dec 13, 2013
    2,449
    428
    why, when you can get a current transformer cheaper, and less complex? there are standard "relay" modules that use current transformers to determine the phase, power factor, and current. it is an industry standard.
     